What is the proper pressure for the tank once the water pump is turned back on? Is it 28 PSI or 50 PSI with a 30/50 pressure switch? If water comes out of the air valve on the top, does that mean the tank is bad?
Back to Top
Art_xyz View Drop Down
Senior Member
Senior Member


Joined: 17-Mar-2000
Location: Salisbury, Md. U.S.A
Points: 152
Direct Link To This Post Posted: 30-Apr-2000 at 12:50pm
If you have a tank with a rubber bladder and you get water out of the air valve, the tank is bad and needs replaced.
Back to Top
kenny b View Drop Down
Newbie
Newbie
Avatar

Joined: 03-Oct-2000
Points: 38
Direct Link To This Post Posted: 30-Apr-2000 at 3:47pm
the correct pressure setting is 2lbs. below the on setting.
Back to Top
daveroconn View Drop Down
Senior Member
Senior Member


Joined: 10-Apr-2000
Location: Phoenix, AZ USA
Points: 221
Direct Link To This Post Posted: 01-May-2000 at 5:04pm
Steve, that tank is dead throw it out. Get a new expasion tank.